NP Environmental gives Central New York homeowners a second opinion on heat pumps that are not heating properly, short cycling or condemned, including systems other companies installed. We service Mitsubishi systems directly and assess other heat pump brands case by case; we do not service conventional gas or oil furnaces or boilers.

What we’re called about

Six symptoms. Rarely a dead unit.

Not heating properly

Rooms never quite get warm, or the system runs constantly and falls behind on cold nights. Usually sizing, airflow, or charge — not a dead unit.

Short cycling

Starts, stops, starts again. Often an oversized system, a control setting, or a restricted filter — all fixable.

Oversized or undersized

Sized off a furnace tag or square footage instead of a heat-loss calculation. We run the Manual J and tell you what the house actually needs.

Installed but never commissioned

No pressure test, no measured evacuation, charge guessed. We measure what should have been measured on day one.

Error codes and lockouts

High-pressure trips, communication faults, defrost issues — diagnosed at the source, with the actual failed component identified.

Can’t reach your installer

Out of business, not answering, or “not our problem.” We answer the phone — even for systems we didn’t install.

What we take on: heat pump systems — geothermal, ducted and ductless air source, and air-to-water. Mitsubishi systems we service directly; other heat pump brands are assessed case by case. We do not service conventional gas or oil furnaces and boilers.

Case study · Thorough Every Time

“Dead from a power surge,” they said. It needed its filter washed.

  1. 1

    She had our proposal. She went with someone cheaper. This summer that installer told her a power surge had killed the unit and every component needed replacing.

  2. 2

    She called us. Our technician reconnected the wiring they had pulled apart and switched it on. It tripped on high pressure. He opened the blower cabinet — so much standing water inside, and so much suction against the panel, he could not lift the cover off. He pulled the filter. It had never once been washed, only vacuumed.

  3. 3

    He rinsed it. The system ran. Nothing was dead. Nothing needed replacing. It needed somebody to look properly.

This is not a rare story. Last winter a homeowner who had bought elsewhere called us because she could not reach her own installer’s service department. We spent twenty-five minutes on the phone walking her through a reset so she had heat that night. She was not our customer. We did it anyway.

Get a second opinion on your system

“You guys quoted us. We got what we paid for.”

A homeowner’s own words, this summer, after a cheaper contractor told her the system was dead

We are not the cheapest company in this county. We are the one that is still answering the phone in year eight. It’s the same reason we take the time on every proposal: our systems are sized properly.

The diagnosis visit

We measure. We don’t guess.

  1. 1Airflow and filters — the cause behind more “dead” systems than any other.
  2. 2Refrigerant charge, by weight — checked against the manufacturer’s figure, not by feel.
  3. 3Sizing against a Manual J — is the system right for this house at Central New York design temperatures?
  4. 4Controls and commissioning readings — settings, sensors, and the numbers that should have been recorded at install.
  5. 5A written finding — what’s wrong, what it takes to fix, and what it doesn’t. Then you decide.

Cheap is expensive. A second opinion is not.

Book a diagnosis visit

We confirm the visit by phone. Weekends are emergency-only — for no heat now, call (315) 841-8730.

By sending this form you agree that NP Environmental may call or email you about your request. Texts only if you tick the box. Consent is not a condition of purchase. We never sell your details. Privacy policy · 4.9★ from 138 Google reviews.

Straight answers

Straight answers about struggling heat pumps

My heat pump isn’t heating properly — is it broken?

Often not. The most common causes are a system sized without a heat-loss calculation, restricted airflow (dirty or never-washed filters), an incorrect refrigerant charge, or controls set for a furnace instead of a heat pump. A proper diagnosis finds the real cause before any part is condemned.

Why is my mini split short cycling?

Short cycling usually points to an oversized system, a thermostat or sensor setting, or airflow restriction. We check sizing against a Manual J calculation, verify airflow and charge, and correct the settings — replacement is rarely the answer.

Do you service heat pumps you didn’t install?

Yes. Mitsubishi systems we service directly as an ELITE Diamond Contractor; other heat pump brands we assess case by case. We do not take on conventional gas or oil furnaces and boilers.

Another company says my unit is dead. Should I get a second opinion?

Yes — and before you sign anything. We have restored “dead” units with a filter cleaning and a reconnected wire. A diagnosis visit costs far less than an unnecessary replacement.

Call (315) 841-8730 Book Free Assessment